  • CVSS v4 8.3
  • Vendor: AVEVA
  • Equipment: Edge
  • Vulnerability: Use of a Broken or Risky Cryptographic Algorithm
Successful exploitation of this vulnerability could allow a local attacker to reverse engineer passwords through brute force.
The following versions of AVEVA Edge (formerly InduSoft Web Studio), a HMI/SCADA software, are affected:
  • Edge: Versions 2023 R2 and prior
3.2.1 USE OF A BROKEN OR RISKY CRYPTOGRAPHIC ALGORITHM CWE-327
The vulnerability, if exploited, could allow a miscreant with read access to Edge Project files or Edge Offline Cache files to reverse engineer Edge users' app-native or Active Directory passwords through computational brute-forcing of weak hashes.
CVE-2025-9317 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.4 has been calculated; the CVSS vector string is (AV:L/AC:L/PR:L/UI:N/S:C/C:H/I:H/A:N).
A CVSS v4 score has also been calculated for CVE-2025-9317. A base score of 8.3 has been calculated; the CVSS vector string is (AV:L/AC:L/AT:N/PR:L/UI:N/VC:H/VI:N/VA:N/SC:H/SI:H/SA:N).
  • COMPANY HEADQUARTERS LOCATION: United Kingdom
Joao Varelas reported this vulnerability to CISA.
AVEVA recommends that organizations evaluate the impact of this vulnerability based on their operational environment, architecture, and product implementation.
Users using the affected product versions should take the following actions to mitigate the risk of exploit:
  • Apply AVEVA Edge 2023 R2 P01 Security Update and migrate old project files.
  • For projects that cannot be migrated (e.g. backups or transient copies), evaluate the risk of potential password leakage from these files and implement stricter read access controls to protect these unsafe files.
  • Require AVEVA Edge users to change their passwords.
  • Important: Edge project migration from older versions to 2023 R2 P01 is one-way due to the change in password hashing algorithms.
The following general defensive measures are recommended:
  • Access Control Lists should be applied to all folders where users will save and load project files.
  • Maintain a trusted chain-of-custody on project files during creation, modification, distribution, and use.
  • Apply data-protection at the project level with a strong master password. For configuration step-by-step refer to AVEVA Edge "Technical Reference Manual" > Project Overview > Configuring Additional Project Settings > Options Tab > Data Protection.
  • If passwords are being used as function parameters inside project documents (such as scripts or worksheets), it is recommended to remove those passwords and use project tags instead. For more information on tags refer to AVEVA Edge "Technical Reference Manual" > Tags and the Tag Database > About Tags and the Project Database.
For information on how to reach AVEVA support for your product, please refer to this link: AVEVA Customer Support.
For more information, see AVEVA's Security Bulletin AVEVA-2025-006 or AVEVA's bulletins page.
  • November 13, 2025: Initial Republication of AVEVA-2025-006
This is a companion discussion topic for the original entry at https://www.cisa.gov/news-events/ics-advisories/icsa-25-317-03